Generator quits after a while
Moderators: BeaconMarineBob, Moderator, BeaconMarineDon
Generator quits after a while
My kohler gen set will quit about an hour or so into running. It starts back up fine but shortly quits after. I have a good amount of water discharged out. I am thinking a faulty temp sensor. Could there be low oil too?
- prowlersfish
- 2025 Gold Support
- Posts: 12723
- Joined: Sat Nov 05, 2005 6:56 pm
- Location: Lower Chesapeake Bay ,Va
Yep, both will do it. If you can find the switches, jump one only after it quits the first time and see if it happens again soon after, then try the other. If it doesn't happen with one of the switches jumped, you've found the system at fault (oil or temp). Now you need to determine if it's the switch or actual condition. An IR temp gun and mechanical oil pressure gauge would help here. Let us know what you find.