F32 Air Conditioner questions

Post by adm1217 »

Hello everyone,

It is finally hot on lake Michigan and my A/C keeps tripping the breaker. Was wonder if anyone had any ideas on where to start trouble shooting? I was thinking maybe low on freon but not sure.

Thanks in advance,

Adam N.
East Chicago Marina
Adam Nuetzel
Fred Knapp
Registered user
Posts: 5
Joined: Sun Mar 20, 2011 3:08 pm
Location: Deerfield Beach Fla.

Post by Fred Knapp »

First thing is to check the filter then the sea straner ,then the water flow from the pump
User avatar
Big D
Ultimate User
Posts: 2876
Joined: Sat May 01, 2010 10:39 pm
Location: Ontario, Canada

Post by Big D »

Trips main breaker or AC breaker? The first thing I would check is that your shore power cord is in good shape. Any signs of overheat?

Is this an AC only unit or AC/heat? If both, does the breaker trip on heat setting too?
She was a 1969 36 ft wooden beauty with big blue 440s that we'll miss forever.
And thanks to the gang, 2012 Trojan Boater Of The Year
User avatar
prowlersfish
2025 Gold Support
2025 Gold Support
Posts: 12723
Joined: Sat Nov 05, 2005 6:56 pm
Location: Lower Chesapeake Bay ,Va

Post by prowlersfish »

How long for it to trip the breaker ?
Boating is good for the soul
77/78 TROJAN F36 Conv.
6BTA Cummins diesels
Life is to short for a ugly boat :D
larryeddington
Ultimate User
Posts: 1876
Joined: Mon Sep 28, 2009 5:08 pm
Location: Canton, TX Boat on TEXOMA

Post by larryeddington »

Tripping breaker is simply caused by over amping of the system. By system I mean to include the power supply wiring as well. The first thing is to check amperage draw of the entire unit while running and make sure it is not on the supply side of power, then check each component, compressor, fan motor etc.

Causes within the unit could be;

High head pressure (low or no condensing water flow, checking the condensing water flow through the heat exchanger, an over charge can cause it as well but would have to be grossly overcharged and if no one has worked on it since it worked not very likely)

Starting capacitor or start relay bad if equipped.

Run Capacitor failure.

Short cycle of the compressor on and off with out a starting capacitor circuit for hard start. Can be thermostat initiated or a helpful user that keeps adjusting the stat. Set it and let it do its job, do not move or click it just enough to turn it off or on then back slightly the other way. Many persons are guilty of this.

Harbor freight has a very good inexpensive ohm ammeter that has clip on tongs so you can just put it around the wires to check amps without touching contacts.

If you are not familiar with refrigeration devices my advice is to go to the pro. That said most people jump to the conclusion that the worst is happening (compressor burnout) the far largest percent of AC problems are in the accessories to the system and not the heart of the system.
Larry Eddington