deck fuel fill bonding question

Post by g36 »

on my 78 f32 i have just installed my new fuel tanks and also new deck fills, replacing the original galvanized with aluminum tanks. i have installed new rubber fuel hose to the deck fills but for safety should these also be connected to the boat bonding system. the tanks are but wasnt sure about the deck fills since using flex hose to them.
also i want to seal the gaps around the fuel hose where it passes through the floor to the engine room and a few other penetrations that i have found. what used to be there looks like it was putty which of course has dried and is useless now is expanding foam an option or something else better/safer? thanks for the comments
1997 CARVER 405
"the BLACK PEARL"

past fleet
1978 F32 SEDAN CHRYSLER 318's

current fleet
1997 seadoo gts
1997 yamaha wave venture
1985 sunbird 18 ft runabout
1968 coronado sailboat 25 ft
sunfish
14' hobie cat
canoe
8ft portabote
User avatar
prowlersfish
2025 Gold Support
2025 Gold Support
Posts: 12725
Joined: Sat Nov 05, 2005 6:56 pm
Location: Lower Chesapeake Bay ,Va

Post by prowlersfish »

The fill should be grounded to the tank .
Boating is good for the soul
77/78 TROJAN F36 Conv.
6BTA Cummins diesels
Life is to short for a ugly boat :D
User avatar
Big D
Ultimate User
Posts: 2876
Joined: Sat May 01, 2010 10:39 pm
Location: Ontario, Canada

Post by Big D »

Ditto Paul. It's a static safety feature while fueling.
She was a 1969 36 ft wooden beauty with big blue 440s that we'll miss forever.
And thanks to the gang, 2012 Trojan Boater Of The Year
User avatar
g36
Moderate User
Posts: 713
Joined: Tue Sep 11, 2007 8:24 am
Location: soddy daisy, tennessee

Post by g36 »

i was thinking that but thought i would ask

what about using the expanding foam etc for filling in floor/bulkhead penetrations?
1997 CARVER 405
"the BLACK PEARL"

past fleet
1978 F32 SEDAN CHRYSLER 318's

current fleet
1997 seadoo gts
1997 yamaha wave venture
1985 sunbird 18 ft runabout
1968 coronado sailboat 25 ft
sunfish
14' hobie cat
canoe
8ft portabote
User avatar
Big D
Ultimate User
Posts: 2876
Joined: Sat May 01, 2010 10:39 pm
Location: Ontario, Canada

Post by Big D »

Expanding foam is commonly used in new boat construction where passing wires, plumbing etc through bulkheads so I say you're good to go.
She was a 1969 36 ft wooden beauty with big blue 440s that we'll miss forever.
And thanks to the gang, 2012 Trojan Boater Of The Year
thelast322
Registered user
Posts: 75
Joined: Sun Jan 14, 2007 5:57 am
Location: Upper Chesepeake Bay MD

Post by thelast322 »

The fuel bonding wire is a USCG code of federal regulation. Resistance between the fuel fill deck connection and tank connection needs to be <100ohms per CFR . ABYC H24.15.1 STATES each metallic plated component of the fuel fill system, and fuel tank, which is in contact with the fuel, shall be grounded so that its resistance to the boats ground is less than 1 ohm.
Also when trying to achieve this ground H24.15.1.2 States---Grounding wires shall be not be clamped between the fill pipes and the flexible hose. This is directly out of the American boat & yacht council Standards book. CFR's are mandatory and Abyc are voluntary requirements unless stated in the CFRs.

So terminate your 8 gauge tinned stranded copper and pull out the fluke meter to see what your readings are.
While we are talking about it, please use double clamps on your fuel fill connections. That also is a mandatory requirement." iam sure you knew that one"
Hope this helps :?
Butch
"Liberty Call"

1991 F32 Crusaders
celebrating 10+years of ownership
User avatar
prowlersfish
2025 Gold Support
2025 Gold Support
Posts: 12725
Joined: Sat Nov 05, 2005 6:56 pm
Location: Lower Chesapeake Bay ,Va

Post by prowlersfish »

Good info Butch .
Boating is good for the soul
77/78 TROJAN F36 Conv.
6BTA Cummins diesels
Life is to short for a ugly boat :D
User avatar
g36
Moderate User
Posts: 713
Joined: Tue Sep 11, 2007 8:24 am
Location: soddy daisy, tennessee

Post by g36 »

bonding it shall be. wire is on order.

spray foam for the gaps thanks

double clamps on the fuel hose. i did that, since i had them on the originals i removed so i put 2 back on my new connections.
thanks for the info guys

the new aluminum tanks looked so nice it was hard to cover them up with the hatch.

i did get the wife to paint the bilge (i helped too)while i had my tanks out. the payment, well that was expensive

i wish i had a glass/acrylic cockpit floor you could then install some cool lights below and see those new tanks and also have a disco floor. what do you think?
1997 CARVER 405
"the BLACK PEARL"

past fleet
1978 F32 SEDAN CHRYSLER 318's

current fleet
1997 seadoo gts
1997 yamaha wave venture
1985 sunbird 18 ft runabout
1968 coronado sailboat 25 ft
sunfish
14' hobie cat
canoe
8ft portabote
paragonremodeling
Registered user
Posts: 1
Joined: Tue Sep 13, 2011 6:36 am
Contact:

Virginia Contractors

Post by paragonremodeling »

Thanks for your post. I like this information,
rossjo
Ultimate User
Posts: 2799
Joined: Tue Nov 08, 2005 2:48 pm
Location: Charleston, SC
Contact:

Post by rossjo »

thelast322 wrote:The fuel bonding wire is a USCG code of federal regulation. Resistance between the fuel fill deck connection and tank connection needs to be <100ohms per CFR . ABYC H24.15.1 STATES each metallic plated component of the fuel fill system, and fuel tank, which is in contact with the fuel, shall be grounded so that its resistance to the boats ground is less than 1 ohm.
Also when trying to achieve this ground H24.15.1.2 States---Grounding wires shall be not be clamped between the fill pipes and the flexible hose. This is directly out of the American boat & yacht council Standards book. CFR's are mandatory and Abyc are voluntary requirements unless stated in the CFRs.

So terminate your 8 gauge tinned stranded copper and pull out the fluke meter to see what your readings are.
While we are talking about it, please use double clamps on your fuel fill connections. That also is a mandatory requirement." iam sure you knew that one"
Hope this helps :?
Butch
Wow - Butch is the man!

Oh - I vote NO on the disco floor .. but would have voted yes 30 years ago!
Captain Ross, 2009 Trojan Boater of the Year
"Viva Mahia" F32 Cummins 6BTA diesels,
"Mack Attack" Chaparral 244 Fish, SeaPro 180, McKee 14, Montauk-17
Image
User avatar
Stripermann2
Ultimate User
Posts: 3027
Joined: Fri Jan 19, 2007 9:11 am
Location: Solomon's Island, MD

Post by Stripermann2 »

Not to get off topic...but where have you been Butch?
Jamie


1985 F-32 270 Crusaders
1988 Sea Ray 23 350 Merc.
Trojan. Enjoy the ride...

-I don't wanna hear anyone whine...Anymore!
-You might get there before me, but you still have to wait for me, for the fun to start!
Rich Schwochow
Registered user
Posts: 58
Joined: Mon Oct 13, 2008 8:36 pm
Location: Wyandotte.Mi.

Fuel Tanks

Post by Rich Schwochow »

What is the gauge of the new aluminium tanks? Some suppliers sell .90 but it is recomended that a minimum of .125 be used for replacements. Just FYI, under the current code of Federal Regulations, Chapter 1 U.S.C.G./Dept. of Homeland Security, Part 182, section182-440 all NEW Construction with aluminium tanks for 1-80 gals. must be a minimum of .250 gauge. Rich
User avatar
g36
Moderate User
Posts: 713
Joined: Tue Sep 11, 2007 8:24 am
Location: soddy daisy, tennessee

Re: Fuel Tanks

Post by g36 »

Rich Schwochow wrote:What is the gauge of the new aluminium tanks? Some suppliers sell .90 but it is recomended that a minimum of .125 be used for replacements. Just FYI, under the current code of Federal Regulations, Chapter 1 U.S.C.G./Dept. of Homeland Security, Part 182, section182-440 all NEW Construction with aluminium tanks for 1-80 gals. must be a minimum of .250 gauge. Rich
my new tanks are 3/16 or 0.1875. i felt the 1/8 was to thin and i couldnt imagine something thinner than that like the .90. with the placement of the original bunks in the boat the company suggested the 3/16. i can stand on the side of them empty with no flexing. i think these will be more than adequate. these guys make tanks for lots of new installs also so im sure they have all their ducks in a row. the coast guard certification plates are on the tanks these will probably out last me
1997 CARVER 405
"the BLACK PEARL"

past fleet
1978 F32 SEDAN CHRYSLER 318's

current fleet
1997 seadoo gts
1997 yamaha wave venture
1985 sunbird 18 ft runabout
1968 coronado sailboat 25 ft
sunfish
14' hobie cat
canoe
8ft portabote
User avatar
prowlersfish
2025 Gold Support
2025 Gold Support
Posts: 12725
Joined: Sat Nov 05, 2005 6:56 pm
Location: Lower Chesapeake Bay ,Va

Re: Fuel Tanks

Post by prowlersfish »

Rich Schwochow wrote:What is the gauge of the new aluminium tanks? Some suppliers sell .90 but it is recomended that a minimum of .125 be used for replacements. Just FYI, under the current code of Federal Regulations, Chapter 1 U.S.C.G./Dept. of Homeland Security, Part 182, section182-440 all NEW Construction with aluminium tanks for 1-80 gals. must be a minimum of .250 gauge. Rich

Can you give a link to this as I can not find any such info ? I asume ou mean .250" not .250 gauge ?
Boating is good for the soul
77/78 TROJAN F36 Conv.
6BTA Cummins diesels
Life is to short for a ugly boat :D
Post Reply