deck fuel fill bonding question
Posted: Sun Jun 19, 2011 9:50 pm
by g36
on my 78 f32 i have just installed my new fuel tanks and also new deck fills, replacing the original galvanized with aluminum tanks. i have installed new rubber fuel hose to the deck fills but for safety should these also be connected to the boat bonding system. the tanks are but wasnt sure about the deck fills since using flex hose to them.
also i want to seal the gaps around the fuel hose where it passes through the floor to the engine room and a few other penetrations that i have found. what used to be there looks like it was putty which of course has dried and is useless now is expanding foam an option or something else better/safer? thanks for the comments
Posted: Sun Jun 19, 2011 10:35 pm
by prowlersfish
The fill should be grounded to the tank .
Posted: Sun Jun 19, 2011 11:10 pm
by Big D
Ditto Paul. It's a static safety feature while fueling.
Posted: Mon Jun 20, 2011 7:41 am
by g36
i was thinking that but thought i would ask
what about using the expanding foam etc for filling in floor/bulkhead penetrations?
Posted: Mon Jun 20, 2011 7:49 pm
by Big D
Expanding foam is commonly used in new boat construction where passing wires, plumbing etc through bulkheads so I say you're good to go.
Posted: Mon Jun 20, 2011 10:56 pm
by thelast322
The fuel bonding wire is a USCG code of federal regulation. Resistance between the fuel fill deck connection and tank connection needs to be <100ohms per CFR . ABYC H24.15.1 STATES each metallic plated component of the fuel fill system, and fuel tank, which is in contact with the fuel, shall be grounded so that its resistance to the boats ground is less than 1 ohm.
Also when trying to achieve this ground H24.15.1.2 States---Grounding wires shall be not be clamped between the fill pipes and the flexible hose. This is directly out of the American boat & yacht council Standards book. CFR's are mandatory and Abyc are voluntary requirements unless stated in the CFRs.
So terminate your 8 gauge tinned stranded copper and pull out the fluke meter to see what your readings are.
While we are talking about it, please use double clamps on your fuel fill connections. That also is a mandatory requirement." iam sure you knew that one"
Hope this helps
Butch
Posted: Tue Jun 21, 2011 6:48 am
by prowlersfish
Good info Butch .
Posted: Tue Jun 21, 2011 7:28 am
by g36
bonding it shall be. wire is on order.
spray foam for the gaps thanks
double clamps on the fuel hose. i did that, since i had them on the originals i removed so i put 2 back on my new connections.
thanks for the info guys
the new aluminum tanks looked so nice it was hard to cover them up with the hatch.
i did get the wife to paint the bilge (i helped too)while i had my tanks out. the payment, well that was expensive
i wish i had a glass/acrylic cockpit floor you could then install some cool lights below and see those new tanks and also have a disco floor. what do you think?
Virginia Contractors
Posted: Tue Sep 13, 2011 6:38 am
by paragonremodeling
Thanks for your post. I like this information,
Posted: Tue Sep 13, 2011 6:09 pm
by rossjo
thelast322 wrote:The fuel bonding wire is a USCG code of federal regulation. Resistance between the fuel fill deck connection and tank connection needs to be <100ohms per CFR . ABYC H24.15.1 STATES each metallic plated component of the fuel fill system, and fuel tank, which is in contact with the fuel, shall be grounded so that its resistance to the boats ground is less than 1 ohm.
Also when trying to achieve this ground H24.15.1.2 States---Grounding wires shall be not be clamped between the fill pipes and the flexible hose. This is directly out of the American boat & yacht council Standards book. CFR's are mandatory and Abyc are voluntary requirements unless stated in the CFRs.
So terminate your 8 gauge tinned stranded copper and pull out the fluke meter to see what your readings are.
While we are talking about it, please use double clamps on your fuel fill connections. That also is a mandatory requirement." iam sure you knew that one"
Hope this helps
Butch
Wow - Butch is the man!
Oh - I vote NO on the disco floor .. but would have voted yes 30 years ago!
Posted: Tue Sep 13, 2011 6:58 pm
by Stripermann2
Not to get off topic...but where have you been Butch?
Fuel Tanks
Posted: Tue Sep 13, 2011 9:12 pm
by Rich Schwochow
What is the gauge of the new aluminium tanks? Some suppliers sell .90 but it is recomended that a minimum of .125 be used for replacements. Just FYI, under the current code of Federal Regulations, Chapter 1 U.S.C.G./Dept. of Homeland Security, Part 182, section182-440 all NEW Construction with aluminium tanks for 1-80 gals. must be a minimum of .250 gauge. Rich
Re: Fuel Tanks
Posted: Tue Sep 13, 2011 10:39 pm
by g36
Rich Schwochow wrote:What is the gauge of the new aluminium tanks? Some suppliers sell .90 but it is recomended that a minimum of .125 be used for replacements. Just FYI, under the current code of Federal Regulations, Chapter 1 U.S.C.G./Dept. of Homeland Security, Part 182, section182-440 all NEW Construction with aluminium tanks for 1-80 gals. must be a minimum of .250 gauge. Rich
my new tanks are 3/16 or 0.1875. i felt the 1/8 was to thin and i couldnt imagine something thinner than that like the .90. with the placement of the original bunks in the boat the company suggested the 3/16. i can stand on the side of them empty with no flexing. i think these will be more than adequate. these guys make tanks for lots of new installs also so im sure they have all their ducks in a row. the coast guard certification plates are on the tanks these will probably out last me
Re: Fuel Tanks
Posted: Wed Sep 14, 2011 6:46 am
by prowlersfish
Rich Schwochow wrote:What is the gauge of the new aluminium tanks? Some suppliers sell .90 but it is recomended that a minimum of .125 be used for replacements. Just FYI, under the current code of Federal Regulations, Chapter 1 U.S.C.G./Dept. of Homeland Security, Part 182, section182-440 all NEW Construction with aluminium tanks for 1-80 gals. must be a minimum of .250 gauge. Rich
Can you give a link to this as I can not find any such info ? I asume ou mean .250" not .250 gauge ?